APC+120amp hours battery=insane uptime?

Anything related to hardware (CPU/MoBo/Video/FSB/BIOS, etc.), hardware settings, overclocking, cooling, cool cases, case mods, hardware mods, post pics of your unique creations here.
Post Reply
touser3
Regular Member
Posts: 151
Joined: Wed Dec 06, 2000 12:00 am

APC+120amp hours battery=insane uptime?

Post by touser3 »

Hi all, i have a 120 Amp Hour/850MCA deep cycle marine battery lying around, and i was thinking to myself "isn't there a way to hook this thing up to my APC for some insane uptime in a power outtage?" My question is, can i do this? The battery is brand new, but i don't know if it is going to overload my apc or if there are any other problems with doing this? Thanks in advance!
User avatar
A_old
Posts: 10663
Joined: Sun Jan 30, 2000 12:00 am
Location: Atlanta

Post by A_old »

dunno but i've seen someone hook 2 car batteries to an apc, so why the heck not lol
User avatar
YARDofSTUF
Posts: 70006
Joined: Sat Nov 11, 2000 12:00 am
Location: USA

Post by YARDofSTUF »

ya just be careful and tell us about it when its done
User avatar
RoundEye
Posts: 18219
Joined: Sun Jul 16, 2000 12:00 am
Location: In a dry but moldy New Orleans, Louisiana

Post by RoundEye »

Some UPS have two batteries in them, in series, which equals 24 volts. If yours has two batteries, then no, you can't do it.

If you only have one battery, then yes you can do it.

Here's the potential problems,

The UPS may be able to keep a good battery charged, but it might overheat the charging system trying to charge a low or dead battery other then what it is rated for, such as would happen after an extended power outage.

Also, almost all UPS's have sealed batteries which emit very little gas. When you charge a standard battery it emits an explosive and corrosive gas simular to hydrogen (remember the Hindenburg?)

If you don't blow yourself up lighting a cigarette, then the corrosion will eat up any organic material within about a six foot area. Such as cotton, steel, ect.

Other then that you should be OK. :D
Sliding down the banister of life ..........................
touser3
Regular Member
Posts: 151
Joined: Wed Dec 06, 2000 12:00 am

Post by touser3 »

Thank you for the reply's everyone! RoundEye, thanks for the info on the gases, i knew about them but not exactly what they where capable of doing..so, basically, my ups only has one battery so that means this should work, also i dont want the ups charging it! What i want to do is just plug it into the ups, fully charged, and after a power outtage i would just detatch it from the ups and carry it outside to charge it with the correct charger... would this work? Also about those gases..would it be better to put the battery in something like an air tight container so that the gases from the battery cant leak out into the room? thanks again!
Post Reply